Andy - PT100s are not like thermocouples at all.
PT100s are passive platinum resistive devices and the measuring circuit passes a known small current through the sensor and then measures the voltage that develops across it. From the voltage and current it can work out the resistance (using Ohms law) and then work out the temperature using a lookup table.
Thermocouples on the other hand are active devices that generate a voltage (relying on the Seebeck effect) themselves that is proportional to the temperature. The measuring circuit just has to measure the voltage rather than drive a current and then measure voltage.
Thermocouples are harder to work with in one way becuase every connection forms a thermocouple junction and can introduce errors which is why it is crucial to minimise the number of connections and if necessary to entend then to use the correct thermocouple cable. TypeK Thermocouples give approximately 41 micro volts per degree C so the measuring circuit has to be very sensitive.
PT100s are driven usually driven with a constant current of 1mA (milli amp) or less and give a larger change in voltage with change in temperature.
Ok, who's nodded off in the back there
Edit: The SSR is mounted to the side of the case with two M4 bolts (heads are countersunk into enclosure).