OK chaps I think there needs to be a bit clarification on some of this.
13A plug/socket as a rule arn't good to take a continual, load of anything above 10A (2.2kW @238V). This is due to the plastics in both plug tops and sockets can't take the heat generated. 13A is the absolute ceiling of a plug during a peak load for a moment
In truth in electrics its best only ever to load a service or plug, upto 80% of its rating as this allows for voltage fluctuation ( In the UK I've metered voltages from 213V-260V), and it also increases the life span of all components due to heat degredation.
For you all that are running 3kW elements they should NOT be on a 13A plug they should have at least a 16A ceeform/comando plug running of a 16A socket. And as Orfy said if you are running 2 3kW elements on a single service it needs to be at least 40A. the other good thing with 16A plugs is they are splash/shower proof, so are better in a environment with water and steam.
Prolix there are 2 or 3 possibilities on why you had a double socket failure.
1) loose terminal/bad termination. on either the live or neutral
2) component failure
3) the rating of the socket. just because of a double you could conciviebly draw 26A, does not mean the socket can cope with 18A current draw for any length of time
I take it that you have 1.8kW/2kW elements from the current you mention.
Also nothing popped in the fuse or breaker front because you were neither overdrawing current (MCB/fuse) and you were not shorting to earth(RCD).
A picture of the offending item would help us locate the fault
footnote, although I am not a qualified sparks in my working life I work with electrics everyday from 63Asingle phase upto thousands of Amps of three phase. And I have picked up from the sparks I work with safe ways to work with electrics to be factored into system design.
Taxi