Ok so I’m being pushed out of the house for brewing and need an extension cable that can take it.
I’ve got a boiler with 2 x2.5kw elements and tried it outside with my normal b&q extension coil. That didn’t work. Came to the boil nicely then the extension cable died and flipped the circuit breaker.
So what do I really need? I need about 10m and have access to the cooker plug if that helps.
As you can probably tell I’m not electrician so please keep it (very) simple.
Thanks very much
Wilf
extension cable
Re: extension cable
Just a quick point to note. When you say you have access to the cooker plug do you mean the cooker switch that has a built in socket next to it? If so this socket is still rated at 13A the same as your normal sockets.
Re: extension cable
You need a 13A cable for each element. Most extension reels are only 10A e.g. Wilko's sell a few but only one is 13A. Probably cheaper to buy suitable cable/two plugs/two sockets (MK would be a good brand) and build a couple like this.
Each cable should go to a separate plug, not both into a double socket. Preferably one into the cooker circuit though a single circuit should be OK if kept below 7kW total (e.g. 2x2.5kW then switch off one if someone wants a 3kW kettle).
edit: if you buy reels, remember to fully unwind them
Each cable should go to a separate plug, not both into a double socket. Preferably one into the cooker circuit though a single circuit should be OK if kept below 7kW total (e.g. 2x2.5kW then switch off one if someone wants a 3kW kettle).
edit: if you buy reels, remember to fully unwind them
I brew therefore I ... I .... forget
-
- Piss Artist
- Posts: 295
- Joined: Sat Jun 30, 2012 4:09 pm
- Location: Half way between Newcastle and Sunderland
Re: extension cable
Thanks both for the help. Cables ordered and on its way. Next step cover to keep out of the rain!
Cheers
Wilf
Cheers
Wilf
-
- Falling off the Barstool
- Posts: 3899
- Joined: Thu Jan 24, 2013 11:07 pm
- Location: South Wales UK.
Re: extension cable
wilfh,
You must buy one of these then!
https://en.wikipedia.org/wiki/Roof
WA
Sorry, Couldn`t resist.
Re: extension cable
The current drawn in Amps is equal to the Wattage divided by Volts. (1KW draws 4A assuming a 250V supply).
If using extension leads ensure they are suitably rated and unwind them fully. If they are used partly unwound they can get very hot and melt.
The best way to use 2 high wattage elements is to connect each one to a different socket, ensuring the two sockets are on different ring mains.
To find which sockets to use flip the trips1 by 1 in your fuse box. Alternatively use one ring main and the cooker socket. Make sure everything
is safely earthed. Hope I have helped, please be careful, get a qualified electrician if in any doubt, (I don't want to be responsible for any problems).
If using extension leads ensure they are suitably rated and unwind them fully. If they are used partly unwound they can get very hot and melt.
The best way to use 2 high wattage elements is to connect each one to a different socket, ensuring the two sockets are on different ring mains.
To find which sockets to use flip the trips1 by 1 in your fuse box. Alternatively use one ring main and the cooker socket. Make sure everything
is safely earthed. Hope I have helped, please be careful, get a qualified electrician if in any doubt, (I don't want to be responsible for any problems).
-
- Even further under the Table
- Posts: 2626
- Joined: Mon Mar 22, 2010 7:10 pm
- Location: Christchurch, Dorset
Re: extension cable
You're unlikely to have two ring mains you can access easily. Nor do you need two rings.hal wrote: ↑Sun Sep 23, 2018 4:41 pmThe current drawn in Amps is equal to the Wattage divided by Volts. (1KW draws 4A assuming a 250V supply).
If using extension leads ensure they are suitably rated and unwind them fully. If they are used partly unwound they can get very hot and melt.
The best way to use 2 high wattage elements is to connect each one to a different socket, ensuring the two sockets are on different ring mains.
To find which sockets to use flip the trips1 by 1 in your fuse box. Alternatively use one ring main and the cooker socket. Make sure everything
is safely earthed. Hope I have helped, please be careful, get a qualified electrician if in any doubt, (I don't want to be responsible for any problems).
Two separate sockets on the same ring will be fine as long as the ring is rated high enough at the consumer unit. For 2 x 2.5kW elements you'd need a fairly chunky breaker. 30 amps would do it. This would then allow other appliances up to about 3kW to run off the ring without tripping it. My downstairs ring is rated at 32 amps. Fairly standard, I think.
Guy
Re: extension cable
5KW will draw about 20A, so 32A ring main will be OK. 32A mcb's are standard in most houses for a ring main.